On Mon, 07 Nov 2005 04:22:50 -0800, Wingedcat wrote:
> I would like some help to understand my CH/HW configuration.
>
> My system is a totally standard open vented fully pumped Y-plan system
> with an indirect mains pressure HW cylinder and 5 radiators. However,
> there is one strange anomoly.
>
> As you might expect the mid position valve is on the flow pipe from the
> boiler, and its two outputs branch off to the Hot Water and the
> Radiator loop.
>
> However, there is a 2-way valve positioned between the HW port of the
> mid-position valve and the connection to the Flow port of the HW tank
> coil. This valve opens when the Call for Heat signal is given to the
> boiler, i.e. HW, CH or Both are demanded by the controller.
>
> At first glance this extra 2-way valve seems completely unnecessary.
> Why has it been put here? What harm can it do? I initially thought it
> could not do any harm if I leave it as it is. However, as the 2-way
> valve is connected to the Call for Heat signal to the boiler and not
> the live signal from the boiler to the pump, it could present a
> problen.
>
> For those that understand 3-way valves, if the valve gets left in the
> HW only position, and the boiler overheat stat fires up the pump,
> (which it does do for a few seconds every time the boiler has been on
> for a while then subsequently turned off), the pump will be asked to
> circulate the water in the HW coil, but won't be able to because the
> extra 2-way valve is shut, therefore straining the pump.
>
> Is this worth worrying about?
>
Reading the other posts I would like to clarify something.
The only time this arrangement comes up is when an unvented cylinder is
retro fitted to an existing heating system that previously used Y-plan.
Anyone starting from scratch would use S-plan controls for sure. Unvented
cylinders are (IME) supplied with a zone valve anyway.
For this arrangement to work correctly the additional zone valve on the
indirect coil must be the sort with a a changeover micro switch (grey,
orange and white wire) so that HW satisfied signal is available for the
3-port valve.
The HW demand is taken through the tank stat to the 2-port valve which
then produces both HW demand and satisfied signals for the 3-port valve.
The boiler sounds like it really needs a bypass circuit which was lost
when the unvented cylinder was installed.
--
Ed Sirett - Property maintainer and registered gas fitter.