In an earlier contribution to this discussion,
Dave Fawthrop <(E-Mail Removed)> wrote:
> I have done some re-piping of my radiators as part of moving to a
> combi boiler. As the new stuff will be pressurized, is it a good
> idea to subject the old, in *good* condition, radiators, old and new
> pipes, to a mains water pressure test?
>
> I will temporarily install a small stop valve in case of problems,
> which I do not anticipate.
If your mains is like mine, it will be at about 4 bar. The normal operating
range of the system will be between 1 and 2 bar - and it's good to test at a
higher pressure (provided you don't overdo it!) to make sure you've got a
safety margin.
AIUI, many new radiators are factory tested at 10 bar - so they will
certainly stand 4 bar if they're ok. If they're not, 4 bar should show up
any rusty pinholes which may be developing. The pipework is presumably very
similar to that used for your domestic cold water water supply - which
clearly *has* to stand mains pressure.
In short, I don't see a problem with what you're proposing.
If you are replacing the boiler, it would be a good time to remove the
radiators, take them outside, and give them a really wash out with a
hosepipe. If I were doing it, I'd rig up a means of doing an initial
pressure test on each rad whilst it is outside before testing the whole
system.
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.
|