Re: urgent - heating pumping over problem

 
 
BB king
Guest
Posts: n/a

 
      01-15-2004, 09:23 PM


>
> Now customer has hot water & central heating. However I noticed that the
> vent pipe for the central heating is constantly running - pumping over,

the
> water in the header tank roasting. This had been going on all day, and
> condensation now dripping off roof in attic. What could cause this to

happen
> to a previously working system?
>
> The vent (22mm) and feed (15mm) pipes connect together within 4" of each
> other at the inlet to the pump. Although the vent is pumping over, the

tank
> is not filling, so the water going in to the tank through the vent must be
> leaving through the feed pipe. It's as if the connection between the two
> pipes at the pump inlet is blocked... only thing I can think of, but

doesn't
> seem likely.
>
> Please help!!
>
> Cheers
> Colin


There is a good chance that the cold feed pipe is blocked up. Check the f&e
tank to see if there is sludge on the bottom, if so, there is a good chance
it will be blocked further down too.
I remember finding a similar problem to this, we replaced the said pipe and
hey presto !! bob's me grannie !!!!)

mike


 
Reply With Quote
 
 
 
 
John Stumbles
Guest
Posts: n/a

 
      01-16-2004, 06:46 PM
"BB king" <robowen(no spam)1@(no spam)v21.me.uk> wrote in message
news:(E-Mail Removed)...
>
>
> >
> > Now customer has hot water & central heating. However I noticed that the
> > vent pipe for the central heating is constantly running - pumping over,

> the
> > water in the header tank roasting. This had been going on all day, and
> > condensation now dripping off roof in attic. What could cause this to

> happen
> > to a previously working system?
> >
> > The vent (22mm) and feed (15mm) pipes connect together within 4" of each
> > other at the inlet to the pump. Although the vent is pumping over, the

> tank
> > is not filling, so the water going in to the tank through the vent must

be
> > leaving through the feed pipe. It's as if the connection between the two
> > pipes at the pump inlet is blocked... only thing I can think of, but

> doesn't
> > seem likely.
> >
> > Please help!!
> >
> > Cheers
> > Colin

>
> There is a good chance that the cold feed pipe is blocked up. Check the

f&e
> tank to see if there is sludge on the bottom, if so, there is a good

chance
> it will be blocked further down too.


That wouldn't cause the reported problem though: there'd be nowhere for the
water being pumped over to go.

I encountered this problem on a system which (a) had the pump set at max -
turning it down stopped it pumping over (b) the opening on the vent pipe was
just an inch or so above the level of water in the header tank, which meant
that as soon as pumping over started it would only require a pressure
difference of 1" WG or so to maintain the flow. This was sorted by
shortening the downturned part of the vent pipe and lowering the level of
water in the tank.



--
John Stumbles
-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-|-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+
-+



 
Reply With Quote
 
 
 
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
* URGENT * HE'S BAAAAACKKKKKKKK * URGENT * WalterChromekite@foxnews.com Home Repair 0 04-05-2010 04:58 AM
CH Pumping Over - Control / Wiring Problem? marc@marc-lee.co.uk Electrical 0 02-26-2006 04:22 PM
Re: urgent - heating pumping over problem Ed Sirett UK DIY 0 01-17-2004 12:20 AM
Re: urgent - heating pumping over problem BigWallop UK DIY 0 01-15-2004 01:38 AM
Re: urgent - heating pumping over problem Set Square UK DIY 1 01-14-2004 11:56 PM


All times are GMT. The time now is 06:44 AM.