> Now customer has hot water & central heating. However I noticed that the
> vent pipe for the central heating is constantly running - pumping over,
the
> water in the header tank roasting. This had been going on all day, and
> condensation now dripping off roof in attic. What could cause this to
happen
> to a previously working system?
>
> The vent (22mm) and feed (15mm) pipes connect together within 4" of each
> other at the inlet to the pump. Although the vent is pumping over, the
tank
> is not filling, so the water going in to the tank through the vent must be
> leaving through the feed pipe. It's as if the connection between the two
> pipes at the pump inlet is blocked... only thing I can think of, but
doesn't
> seem likely.
>
> Please help!!
>
> Cheers
> Colin
There is a good chance that the cold feed pipe is blocked up. Check the f&e
tank to see if there is sludge on the bottom, if so, there is a good chance
it will be blocked further down too.
I remember finding a similar problem to this, we replaced the said pipe and
hey presto !! bob's me grannie !!!!

)
mike