In article <3f250565$0$3135$(E-Mail Removed)>,
John Greenwood <(E-Mail Removed)> wrote:
> What are the options available to me to wire up a cooker hood, I can think
> of three ways but whether these are allowed/legal I do not know:


> 1. Wire it into the lighting circuit, but then there is no accessible
> isolating switch.


Neither is there for most lights. It presumably has its own on off switch?

> 2. Wire it into an FCU hidden behind the hood, but then do I also need an
> accessible isolating switch?


Is it possible to wire it such that the cable comes out of the wall into
it - ie behind it? If the cable comes out the top say near the back it's
often the tidiest way to use an FCU or at least cord outlet even when
wired off the lighting circuit.

> 3. Wire it into the big red cooker switch.


Not a good idea, IMHO.

> I don't really want any visible wiring or socket/FCU. I favour number 2,
> but I don't fancy adding a separate isolating switch as well.


Can't see why you'd need one.

> Anybody help with this?


--
*A bartender is just a pharmacist with a limited inventory.

Dave Plowman (E-Mail Removed) London SW 12
RIP Acorn
 
Reply With Quote
 
 
 
 
Andrew Gabriel
Guest
Posts: n/a

 
      07-28-2003, 01:35 PM
In article <(E-Mail Removed)>,
Dave Plowman <(E-Mail Removed)> writes:
> In article <3f250565$0$3135$(E-Mail Removed)>,
> John Greenwood <(E-Mail Removed)> wrote:
>> What are the options available to me to wire up a cooker hood, I can think
>> of three ways but whether these are allowed/legal I do not know:

>
>> 1. Wire it into the lighting circuit, but then there is no accessible
>> isolating switch.

>
> Neither is there for most lights. It presumably has its own on off switch?


....but you need a means of isolating appliances containing
motors.

You could use an FCU or an unfused double pole switch,
or a bathroom fan isolating switch (ignoring the 3rd
pole, but it will have an appropriate legend on it).
Some cooker hoods have quite high power fans nowadays,
so check the loading on your lighting circuit first.

>> 2. Wire it into an FCU hidden behind the hood, but then do I also need an
>> accessible isolating switch?


You need to be able to operate it for maintenance of the
cooker hood, i.e. before you open or take the hood down.
It doesn't need to be accessible for normal day-to-day use.
If it's far enough away (or out of sight) of the cooker hood
such that someone working on the hood could not be said to
be in direct control of it, it needs to be a type of switch
which can be locked off. Bathroom fan isolating switches
are often of this type, although they don't come with the
lock (it engages in two tiny holes either side of the
rocker, which you probably haven't noticed unless you looked
for them, holding it in the off position).

BTW, and plug and socket is also acceptable means of
isolation.

>> 3. Wire it into the big red cooker switch.

>
> Not a good idea, IMHO.


My cooker circuit has been turned into a switched radial
circuit by fitting 3 socket outlets in place of the
original hardwired cooker outlet. One has the oven plugged
in, another has the gas hob ignition plugged in and the
third was for some appliance previous occupant must have
had in the cupboard under the oven. If your oven plugs
into a 13A socket and you don't have electric hob, I see
nothing wrong in doing this.

--
Andrew Gabriel
 
Reply With Quote
 
 
 
 
Andrew Gabriel
Guest
Posts: n/a

 
      07-28-2003, 03:59 PM
In article <3f2539f3$0$18489$(E-Mail Removed)> ,
"Christian McArdle" <(E-Mail Removed)> writes:
>>My cooker circuit has been turned into a switched radial
>>circuit by fitting 3 socket outlets in place of the
>>original hardwired cooker outlet.

>
> Provided the MCB/fuse is of a sensible rating, of course. (i.e. a 32A or 20A
> B curve). This will usually be the case, although frequently cooker circuits


It is in this case, and 6mm˛ cable.

> are wired with higher ratings, such as 40A or 45A, which would need swapping
> out. Also, you'll need to prove that the sockets aren't likely to be used
> for outdoor portable equipment, as they would need an RCD/RCBO.


Well, there aren't any RCD's in this house at the moment.
If I get round to it before Part P comes into force, I will fit
a nice new CU with separate RCD protection on each ring, and take
the immersion heater off the ring circuit. If I don't get round
to it in time, it will stay with no RCD protection and with the
immersion heater on the ring circuit forever more, or until it
causes a fire and burns the house down...

--
Andrew Gabriel
 
Reply With Quote
 
John Greenwood
Guest
Posts: n/a

 
      07-28-2003, 07:17 PM
Hi Andrew,

Thanks for your reply. I have decided to do the following:

Install a 13A socket behind the cooker hood which will be completely hidden.
The cooker hood will be plugged into this. The socket will be connected to a
visible FCU at worktop level. The FCU being on the kitchen ring circuit.

Does this sound as if it is in line with the regulations?

Thanks,

John

"Andrew Gabriel" <(E-Mail Removed)> wrote in message
news:bg38r3$5r6$(E-Mail Removed)...
> In article <(E-Mail Removed)>,
> Dave Plowman <(E-Mail Removed)> writes:
> > In article <3f250565$0$3135$(E-Mail Removed)>,
> > John Greenwood <(E-Mail Removed)> wrote:
> >> What are the options available to me to wire up a cooker hood, I can

think
> >> of three ways but whether these are allowed/legal I do not know:

> >
> >> 1. Wire it into the lighting circuit, but then there is no accessible
> >> isolating switch.

> >
> > Neither is there for most lights. It presumably has its own on off

switch?
>
> ...but you need a means of isolating appliances containing
> motors.
>
> You could use an FCU or an unfused double pole switch,
> or a bathroom fan isolating switch (ignoring the 3rd
> pole, but it will have an appropriate legend on it).
> Some cooker hoods have quite high power fans nowadays,
> so check the loading on your lighting circuit first.
>
> >> 2. Wire it into an FCU hidden behind the hood, but then do I also need

an
> >> accessible isolating switch?

>
> You need to be able to operate it for maintenance of the
> cooker hood, i.e. before you open or take the hood down.
> It doesn't need to be accessible for normal day-to-day use.
> If it's far enough away (or out of sight) of the cooker hood
> such that someone working on the hood could not be said to
> be in direct control of it, it needs to be a type of switch
> which can be locked off. Bathroom fan isolating switches
> are often of this type, although they don't come with the
> lock (it engages in two tiny holes either side of the
> rocker, which you probably haven't noticed unless you looked
> for them, holding it in the off position).
>
> BTW, and plug and socket is also acceptable means of
> isolation.
>
> >> 3. Wire it into the big red cooker switch.

> >
> > Not a good idea, IMHO.

>
> My cooker circuit has been turned into a switched radial
> circuit by fitting 3 socket outlets in place of the
> original hardwired cooker outlet. One has the oven plugged
> in, another has the gas hob ignition plugged in and the
> third was for some appliance previous occupant must have
> had in the cupboard under the oven. If your oven plugs
> into a 13A socket and you don't have electric hob, I see
> nothing wrong in doing this.
>
> --
> Andrew Gabriel



 
Reply With Quote
 
Andrew Gabriel
Guest
Posts: n/a

 
      07-28-2003, 07:36 PM
In article <3f25766f$0$11385$(E-Mail Removed)>,
"John Greenwood" <(E-Mail Removed)> writes:
> Hi Andrew,
>
> Thanks for your reply. I have decided to do the following:
>
> Install a 13A socket behind the cooker hood which will be completely hidden.
> The cooker hood will be plugged into this. The socket will be connected to a
> visible FCU at worktop level. The FCU being on the kitchen ring circuit.
>
> Does this sound as if it is in line with the regulations?


Yes, but you don't need the FCU.
If the plug can't be withdrawn without first dismantling or
removing the extractor fan, then a double pole 20A switch
will do (unfused as there is a fuse in the 13A plug).
If you can get to the plug for such maintenance, then you
don't even need the switch. You don't need to be able to get
to the plug or switch easily for everyday use -- they are
isolating switches for maintenance, and not required for
functional switching (hood presumably has its own switches
built-in for that).

--
Andrew Gabriel
 
Reply With Quote
 
John Greenwood
Guest
Posts: n/a

 
      07-28-2003, 09:26 PM
Thanks Andrew, all a lot clearer now.

"Andrew Gabriel" <(E-Mail Removed)> wrote in message
news:bg3tvg$d1u$(E-Mail Removed)...
> In article <3f25766f$0$11385$(E-Mail Removed)>,
> "John Greenwood" <(E-Mail Removed)> writes:
> > Hi Andrew,
> >
> > Thanks for your reply. I have decided to do the following:
> >
> > Install a 13A socket behind the cooker hood which will be completely

hidden.
> > The cooker hood will be plugged into this. The socket will be connected

to a
> > visible FCU at worktop level. The FCU being on the kitchen ring circuit.
> >
> > Does this sound as if it is in line with the regulations?

>
> Yes, but you don't need the FCU.
> If the plug can't be withdrawn without first dismantling or
> removing the extractor fan, then a double pole 20A switch
> will do (unfused as there is a fuse in the 13A plug).
> If you can get to the plug for such maintenance, then you
> don't even need the switch. You don't need to be able to get
> to the plug or switch easily for everyday use -- they are
> isolating switches for maintenance, and not required for
> functional switching (hood presumably has its own switches
> built-in for that).
>
> --
> Andrew Gabriel



 
Reply With Quote
 
Andrew McKay
Guest
Posts: n/a

 
      07-28-2003, 09:56 PM
On Mon, 28 Jul 2003 20:17:28 +0100, "John Greenwood"
<(E-Mail Removed)> wrote:

>Install a 13A socket behind the cooker hood which will be completely hidden.
>The cooker hood will be plugged into this. The socket will be connected to a
>visible FCU at worktop level. The FCU being on the kitchen ring circuit.


I think I might be a little concerned about the environment that would
exist behind the cooker hood. By virtue of the fact it is a cooker
hood one expects the general area to get a bit warm, and maybe laced
with condensation/steam and other environmentally unfriendly options.

That probably doesn't make it a problem for the regs as such, but page
2 of Electrical Commonsense #101 might apply.

The other issue I would raise in this situation is that if you needed
to take the power off that cooker hood fast, do you intend that the
cooker hood has to be stripped before the mains to it can be
disconnected? If so, that doesn't sound like an ideal situation. It'll
be a right royal pain in the butt if the fuse to the cooker hood blows
and you've got to take the whole thing apart to check it out!

Andrew

Do you need a handyman service? Check out our
web site at http://www.handymac.co.uk
 
Reply With Quote
 
BigWallop
Guest
Posts: n/a

 
      07-28-2003, 10:39 PM

"John Greenwood" <(E-Mail Removed)> wrote in message
news:3f259562$0$18489$(E-Mail Removed) ...
> But hang on, can I place a 20A switch in the ring circuit just like a FCU?
>

<snipped>

You won't need any FCU in the circuit if you're making the socket in as part
of the ring main. If you're making the socket for the cooker hood a spur
off from the ring main in the kitchen, then a fused spur unit can be placed
beside the socket where you're taking the spur from. Then you take a single
cable up to the socket behind the cooker hood.

As long as the cooker hood can be completely isolated from the electric's,
both live and neutral, for maintenance reasons, then that is all that is
needed. This is why Andrew recommended either a double pole switch which
breaks both live and neutral supply, or a switched fused spur if you were
removing the plug.

A switched fused spur with flex outlet would be the neatest way, as this
means you're only taking one cable from the existing ring circuit, and
connecting the flex in to the switched fused spur, which is quite within the
regulations.


 
Reply With Quote
 
Andrew Gabriel
Guest
Posts: n/a

 
      07-28-2003, 11:41 PM
In article <3f259562$0$18489$(E-Mail Removed)>,
"John Greenwood" <(E-Mail Removed)> writes:
> But hang on, can I place a 20A switch in the ring circuit just like a FCU?


Yes, switching the spur (and not breaking the ring;-)
You have to have a fuse somewhere, be it in a FCU or in the
appliance plugtop, but you don't need more than one, and
it doesn't have to be at the beginning of the spur.

--
Andrew Gabriel
 
Reply With Quote
 
Andrew McKay
Guest
Posts: n/a

 
      07-29-2003, 11:42 AM
On Tue, 29 Jul 2003 09:22:48 +0100, "John Greenwood"
<(E-Mail Removed)> wrote:

>Point taken Andrew, but how do I wire it so that no plugs/sockets/cables are
>visible?


Maybe a couple of ideas:

1) Take the cable thru one of the cupboards at the side of the cooker
hood, and have the socket in there (you do have a side cupboard to the
cooker hood?).

2) Channel down to beneath the work surface, and put the connection in
a cupboard under there.

3) Take the connection up and to the side, wired into a fused spur.

Andrew

Do you need a handyman service? Check out our
web site at http://www.handymac.co.uk
 
Reply With Quote
 
 
 
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wiring a cooker hood alamaison UK DIY 0 12-18-2011 08:43 PM
Cooker Hood Control Unit WIring beurling Electrical 0 08-03-2011 01:47 PM
wiring chimney style cooker hood:power socket inside chimney noos999@yahoo.co.uk Electrical 6 12-18-2006 07:19 PM
Cooker hood wiring again! John Greenwood Electrical 3 07-31-2003 10:10 AM
Re: cooker hood wiring Toby Electrical 0 07-16-2003 11:23 PM


All times are GMT. The time now is 05:18 PM.