No: regs continue to assume a degree of sense on the part of the drill
holder ;-) It continues to be OK to run cables simply buried in the plaster,
*provided* they're in a direct horiozontal or vertical line from a visible
fitting; or in a couple of well-defined narrow strips - horizontal within
6inches of the wall-ceiling corner, and 6ins either side of the corners of
the room. Other routes require the cable to be either more than 2 inches
deep from the surface of the wall, or to have extra protection against
nailing/drilling. (The idea is to protect against "foreseeable" wall
penetration - picture pins and drill-holes for normal-size wallplugs.
The belief is that heftier works will be undertaken with due care...)
Many people find that even the cheap cable detectors work quite well,
especially when there's current flowing in the cable. (Detecting wooden
studs reliably isn't as well done by cheap scanners; but metal, expecially
with dancing electrons, is easier.)