Electric baseboard heating problem

 
 
Gm1234
Guest
Posts: n/a

 
      12-31-2006, 09:27 PM
We have a bedroom in attic that we seldom use. But with holiday houseguests
it is getting use. But, the electric baseboard heater is not working.

We have fuse panels. This particular room's heating is not identified, but
perhaps it shares a circuit with another heater? Anyway, I removed all fuses
and checked each one. No bad fuses.

The heater is controlled by a wall thermostat - It has white and black wires
coming to it - The thermostat breaks the white wire only, the black wire
really just passes through. I checked voltages - nothing across the white &
black on either side of the thermostat. But from either black or white to
ground (the box), I get 110v. Just is case, I changed out the thermostat for
a spare, but no change.

At heater, it is the same - no voltage between the incoming wires, but 110v
to ground from either side.

Questions:
- If I see 110v to ground from black & white, why don't I see 220V across
these conductors?
- If I see the 110v to ground, does that mean that I do have power to the
heater?

Any suggestions as to how to further troubleshoot this problem?

Graham
Ontario, Canada




 
Reply With Quote
 
 
 
 
dpb
Guest
Posts: n/a

 
      01-01-2007, 12:55 AM

Big Al wrote:
> "dpb" <(E-Mail Removed)> wrote in message
> news:(E-Mail Removed) oups.com...

,,,
> > > This is what I would have thought, but the puzzle is that I get the 110v

> to
> > > ground, but not 220v across the hot conductors. ...

> >
> > That indicates both "hot" wires are connected to the same phase
> > somewhere -- either at the fuse box or at some other junction box,
> > somebody made a wiring mistake and got both of them on the same side.

>
> It indicates one leg is open. The 120 is passing thru the element.


Depends on where he's measuring, but possible, yes. Thought OP
indicated directly across feeds, but if not...

 
Reply With Quote
 
 
 
 
Gm1234
Guest
Posts: n/a

 
      01-01-2007, 01:56 AM

"mm" wrote >
> >We have a bedroom in attic that we seldom use. But with holiday

houseguests
> >it is getting use. But, the electric baseboard heater is not working.

>
> BTW, has it ever worked? How long have you lived there?


Good Question! and the answer is YES it has always worked in the past, but
we had not checked it this winter until now.

This should answer most of the suggestions (I appreciate them!) - We have
lived here for 30+ years - The panel has not been modified during that time
nor the bedroom's wiring.

I understand how the voltages would be as measured if somehow both hots were
being fed from same phase - But at a loss to know how this could be.

We did have some bathroom rewiring done this past summer, but it should not
affect this area. But you never know!

Graham


 
Reply With Quote
 
Gm1234
Guest
Posts: n/a

 
      01-01-2007, 02:02 AM

"dpb" <(E-Mail Removed)> wrote
>
> Big Al wrote:


> >
> > It indicates one leg is open. The 120 is passing thru the element.

>
> Depends on where he's measuring, but possible, yes. Thought OP
> indicated directly across feeds, but if not...
>


I measured zero volts across white/black hot wires at feed to wall
thermostat and also at feed to heater itself. At both places, I read 110v to
ground from either hot wire.

Graham


 
Reply With Quote
 
indago
Guest
Posts: n/a

 
      01-01-2007, 02:51 AM
061231 2102 - Gm1234 posted:

>
> "dpb" <(E-Mail Removed)> wrote
>>
>> Big Al wrote:

>
>>>
>>> It indicates one leg is open. The 120 is passing thru the element.

>>
>> Depends on where he's measuring, but possible, yes. Thought OP
>> indicated directly across feeds, but if not...
>>

>
> I measured zero volts across white/black hot wires at feed to wall
> thermostat and also at feed to heater itself. At both places, I read 110v to
> ground from either hot wire.
>
> Graham
>
>

Disconnect the power to the heater at the panel, and then disconnect the
wires at the heater. Then, reconnect the power to the circuit at the panel,
and turn the thermostat all the way up. Then, check, with your voltmeter,
across the two wires at the heater. Also, check each one to ground. The
one that shows 0 to ground is the one that is giving you the problem. If
the system was working before, it should work now, except maybe a fuse has
blown, or, when the remodel was taking place, the wire got cut somewhere
along the line.

 
Reply With Quote
 
RBM
Guest
Posts: n/a

 
      01-01-2007, 03:45 AM
He should first check to see that he has 240 volts on that circuit at the
panel



"indago" <(E-Mail Removed)> wrote in message
news:C1BDE1CA.7156%(E-Mail Removed)...
> 061231 2102 - Gm1234 posted:
>
>>
>> "dpb" <(E-Mail Removed)> wrote
>>>
>>> Big Al wrote:

>>
>>>>
>>>> It indicates one leg is open. The 120 is passing thru the element.
>>>
>>> Depends on where he's measuring, but possible, yes. Thought OP
>>> indicated directly across feeds, but if not...
>>>

>>
>> I measured zero volts across white/black hot wires at feed to wall
>> thermostat and also at feed to heater itself. At both places, I read 110v
>> to
>> ground from either hot wire.
>>
>> Graham
>>
>>

> Disconnect the power to the heater at the panel, and then disconnect the
> wires at the heater. Then, reconnect the power to the circuit at the
> panel,
> and turn the thermostat all the way up. Then, check, with your voltmeter,
> across the two wires at the heater. Also, check each one to ground. The
> one that shows 0 to ground is the one that is giving you the problem. If
> the system was working before, it should work now, except maybe a fuse has
> blown, or, when the remodel was taking place, the wire got cut somewhere
> along the line.
>



 
Reply With Quote
 
mm
Guest
Posts: n/a

 
      01-01-2007, 04:53 AM
On Sun, 31 Dec 2006 20:56:19 -0500, "Gm1234" <(E-Mail Removed)>
wrote:

>
>"mm" wrote >
>> >We have a bedroom in attic that we seldom use. But with holiday

>houseguests
>> >it is getting use. But, the electric baseboard heater is not working.

>>
>> BTW, has it ever worked? How long have you lived there?

>
>Good Question! and the answer is YES it has always worked in the past, but
>we had not checked it this winter until now.


Hard to believe it used to be connected to the right phase, and it
moved during the summer.
>
>This should answer most of the suggestions (I appreciate them!) - We have
>lived here for 30+ years - The panel has not been modified during that time
>nor the bedroom's wiring.
>
>I understand how the voltages would be as measured if somehow both hots were
>being fed from same phase - But at a loss to know how this could be.
>
>We did have some bathroom rewiring done this past summer, but it should not
>affect this area. But you never know!


That is undoubtedly the reason. How, I have no idea.

You didn't answer my previous post. Is it permanent heating or space
heating? More importantly, do you know that it is 220, or might it be
110?

If it were 110 and the heat is on, but the white is broken some place
between the thermostat and the fusebox, then you would get 110 at both
the whiite and black between ground, but 0 between white and black.

Although white is usually neutral and at ground potential, when the
white wire is broken, the 110 potential will flow from the black
through the appliance to the portion of white closer to the appliance.
It's all at the same voltage when there is no current flow.

Come to think of it, this would all be true with 220 also. In 220
only 110 comes from each conductor. Maybe the fuse or breaker, or
wire, for white or black, is blown, tripped, or broken. That would
account for your symptoms.

>Graham
>


 
Reply With Quote
 
Gm1234
Guest
Posts: n/a

 
      01-01-2007, 04:17 PM
> He should first check to see that he has 240 volts on that circuit at the
> panel


OK, thanks for input - Problem is resolved!

Because heating circuits are not clearly labeled on fuse panel, I did not
know which one the problem heater was on. Today I pulled all heater fuses
(They are in double-fuse holders with hinged cover to prevent removal of
individual fuses). I now did not have 110v to ground at the wall
thermostat. We then plugged the fuseholders in one at a time until the 110v
re-appeared. So we found which circuit the heater was on..

I tested problem circuit fuses by using resistance meter across the brass
forks of the fuse holder and it showed continuity for both pairs. But, when
I removed the fuses, one was bad! This despite it showing no sign of having
blown - fuse strip was still intact - problem must have been internal.

Anyway, a new fuse solved problem - I guess next time I should remove each
fuse from holder, but still don't understand why testing across the "prongs"
showed no problem!

Existing main panel is Amalgamated Electric Cat No 200-4240 combination
service entrance/panel 200A with 19 double fuses and one large fuse pair for
range. There are two small sub panels with 6 breakers each that serve areas
that were re-wired at one time. There is another breaker panel in the garage
also fed from the main panel.

Would it be worthwhile considering upgrading main panel to a breaker panel?
Rough cost?

Thanks for all the input guys!


 
Reply With Quote
 
 
 
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
electric baseboard versus in-floor heating rlz Home Repair 8 02-20-2010 07:04 AM
Repairing electric baseboard heating amyyd Electrical 1 02-19-2007 08:39 PM
Need to replace Electric Baseboard Heating Units & Replacement Windows Mike Electrical 106 02-10-2007 01:05 AM
Need to replace Electric Baseboard Heating Units & Replacement Windows Mike HVAC 93 02-08-2007 01:32 AM
Hydronic elecric baseboard heater vs standard electric baseboard heater John Sevinsky Electrical 16 03-09-2006 04:09 PM


All times are GMT. The time now is 10:57 PM.