      02-12-2004, 10:38 PM
Hi all,

I live in the attic of a house which has been converted into flats.
During the decoration (ahem) of the lounge, I've opened up a storage
space under one of the eaves, which was previously closed off. Before
I board out this space, I think I ought to meet current building regs
with regard to creating a fire compartment here. As this is a
three-storey flat conversion, the building regs say that 30 minutes
`could' be acceptable here.

The space has a suspended ceiling (belonging to the flat below) about
1m underneath it.

So, my question is: will 9.5mm of plasterboard and 18mm of chipboard,
plus the suspended ceiling below, give me the 30 mins fire resistance
I require? What about 18mm of chipboard alone? Or is this one for the
local BCO? :-)

Ben.
 
Reply With Quote
 
 
 
 
Peter Parry
Guest
Posts: n/a

 
      02-12-2004, 11:03 PM
On 12 Feb 2004 14:38:38 -0800, (E-Mail Removed) (Ben
Schofield) wrote:


>The space has a suspended ceiling (belonging to the flat below) about
>1m underneath it.
>
>So, my question is: will 9.5mm of plasterboard and 18mm of chipboard,
>plus the suspended ceiling below, give me the 30 mins fire resistance
>I require?


If you are going over someone elses property then no matter what the
BR say think of your own security. Make sure the compartment is
smoke proof for a start - fires rarely kill - their combustion
product beat them to it. It used to be that a double layer of
plasterboard was adequate to give 30 min resistance - I'm not sure if
this is still so but it isn't far out.

The suspended ceiling should be ignored in any fire resistance
estimations.

>What about 18mm of chipboard alone?


No.

--
Peter Parry.
http://www.wpp.ltd.uk/
 
Reply With Quote
 
 
 
 
Ben Schofield
Guest
Posts: n/a

 
      02-13-2004, 11:48 AM
On Thu, 12 Feb 2004 23:03:57 +0000, Peter Parry <(E-Mail Removed)>
wrote:

> >The space has a suspended ceiling (belonging to the flat below) about
> >1m underneath it.
> >
> >So, my question is: will 9.5mm of plasterboard and 18mm of chipboard,
> >plus the suspended ceiling below, give me the 30 mins fire resistance
> >I require?

>
> If you are going over someone elses property then no matter what the
> BR say think of your own security. Make sure the compartment is
> smoke proof for a start - fires rarely kill - their combustion
> product beat them to it. It used to be that a double layer of
> plasterboard was adequate to give 30 min resistance - I'm not sure if
> this is still so but it isn't far out.


Thanks Peter, I hadn't thought of that. I'll fill the gaps between the
joists, that ought to do it smoke-wise...

Googling, I think that the floors in the rest of the flat have been
filled with something called `foamed perlite', which apparently has 60
minutes fire resistance, so I'd better meet that in the new
compartment too...

Ben.
 
Reply With Quote
 
Peter Taylor
Guest
Posts: n/a

 
      02-13-2004, 12:41 PM
Peter Parry wrote
> On 12 Feb 2004 14:38:38 -0800, (E-Mail Removed) (Ben
> Schofield) wrote:
>
>
> >The space has a suspended ceiling (belonging to the flat below) about
> >1m underneath it.
> >
> >So, my question is: will 9.5mm of plasterboard and 18mm of chipboard,
> >plus the suspended ceiling below, give me the 30 mins fire resistance
> >I require?

>
> If you are going over someone elses property then no matter what the
> BR say think of your own security. Make sure the compartment is
> smoke proof for a start - fires rarely kill - their combustion
> product beat them to it. It used to be that a double layer of
> plasterboard was adequate to give 30 min resistance - I'm not sure if
> this is still so but it isn't far out.
>
> The suspended ceiling should be ignored in any fire resistance
> estimations.


Assuming the original conversion work complied with Building Regulations, I
would be extremely surprised if the 30 minute FR compartmentation covered only
the area within the eaves voids. Normally it would extend to the outside walls
all round. This, coupled with sound insulation, is probably the reason why
there is a suspended ceiling at all. But, either way, here's a thought - if you
provide 30 minute FR doors to the void areas there will be no need to upgrade
the ceiling anyway.

The British Gypsum website http://www.british-gypsum.com/immediacy-824 gives FR
figures for various configuations of plasterboards/joists/floorboards etc.

I don't think it is strictly necessary to apply for Building Regulations
permission to do this work. Providing access to eaves voids, if only for
maintenance, is normal procedure and this is usually through the short walls at
attic level, rather than through the ceiling below. However, it's probably wise
to ask the Building Control office for their views as there may be special
circumstances here. They may even have kept archived records of the conversion
work itself.

Peter

 
Reply With Quote
 
River Tramp
Guest
Posts: n/a

 
      02-13-2004, 09:23 PM
I would have said that to achieve 30min FR with a ceiling of 9.5mm pb, you
need t & g boarding, and the floor void needs 60mm mineral wool on chicken
wire mesh stapled to the joists. For FR purposes only, in the voids you
could do away with the boarding and use 100mm mineral wool instead (but not
if sound insulation is required).

We also would not accept the FR door into the voids; inlike some BC
authorities, we required the entire floor eaves to eaves to have the full
fire resistance. Nowadays all authorities would require the voids boarded
out for sound insulation purposes (eg when doing a loft conversion).

RT



"Peter Taylor" <(E-Mail Removed)> wrote in message
news:Ky3Xb.2843$(E-Mail Removed)...
> Peter Parry wrote
> > On 12 Feb 2004 14:38:38 -0800, (E-Mail Removed) (Ben
> > Schofield) wrote:
> >
> >
> > >The space has a suspended ceiling (belonging to the flat below) about
> > >1m underneath it.
> > >
> > >So, my question is: will 9.5mm of plasterboard and 18mm of chipboard,
> > >plus the suspended ceiling below, give me the 30 mins fire resistance
> > >I require?

> >
> > If you are going over someone elses property then no matter what the
> > BR say think of your own security. Make sure the compartment is
> > smoke proof for a start - fires rarely kill - their combustion
> > product beat them to it. It used to be that a double layer of
> > plasterboard was adequate to give 30 min resistance - I'm not sure if
> > this is still so but it isn't far out.
> >
> > The suspended ceiling should be ignored in any fire resistance
> > estimations.

>
> Assuming the original conversion work complied with Building Regulations,

I
> would be extremely surprised if the 30 minute FR compartmentation covered

only
> the area within the eaves voids. Normally it would extend to the outside

walls
> all round. This, coupled with sound insulation, is probably the reason

why
> there is a suspended ceiling at all. But, either way, here's a thought -

if you
> provide 30 minute FR doors to the void areas there will be no need to

upgrade
> the ceiling anyway.
>
> The British Gypsum website http://www.british-gypsum.com/immediacy-824

gives FR
> figures for various configuations of plasterboards/joists/floorboards etc.
>
> I don't think it is strictly necessary to apply for Building Regulations
> permission to do this work. Providing access to eaves voids, if only for
> maintenance, is normal procedure and this is usually through the short

walls at
> attic level, rather than through the ceiling below. However, it's

probably wise
> to ask the Building Control office for their views as there may be special
> circumstances here. They may even have kept archived records of the

conversion
> work itself.
>
> Peter
>



 
Reply With Quote
 
Peter Taylor
Guest
Posts: n/a

 
      02-14-2004, 10:32 AM

"River Tramp" <(E-Mail Removed)> wrote in message
news:402d40bb$0$6850$(E-Mail Removed). ..
> I would have said that to achieve 30min FR with a ceiling of 9.5mm pb, you
> need t & g boarding, and the floor void needs 60mm mineral wool on chicken
> wire mesh stapled to the joists.


According to British Gypsum White Book (Section c60 page 5), min 18mm T&G
boarding, 47mm thick joists at 450c/c and 9.5mm wallboard with 2mm skim finish
gives 30 minutes FR. No quilt is needed.
http://www.british-gypsum.com/PDF/c60_093.pdf

> For FR purposes only, in the voids you
> could do away with the boarding and use 100mm mineral wool instead (but not
> if sound insulation is required).
>
> We also would not accept the FR door into the voids; inlike some BC
> authorities, we required the entire floor eaves to eaves to have the full
> fire resistance.


That's what I would expect too. I'd be surprised if any extra fire resistance
is needed in the voids.

Peter

 
Reply With Quote
 
Nick Brooks
Guest
Posts: n/a

 
      02-16-2004, 10:21 AM
Peter Parry wrote:
> On 12 Feb 2004 14:38:38 -0800, (E-Mail Removed) (Ben
> Schofield) wrote:
>
>
>
>>The space has a suspended ceiling (belonging to the flat below) about
>>1m underneath it.
>>
>>So, my question is: will 9.5mm of plasterboard and 18mm of chipboard,
>>plus the suspended ceiling below, give me the 30 mins fire resistance
>>I require?

>
>
> If you are going over someone elses property then no matter what the
> BR say think of your own security. Make sure the compartment is
> smoke proof for a start - fires rarely kill - their combustion
> product beat them to it. It used to be that a double layer of
> plasterboard was adequate to give 30 min resistance - I'm not sure if
> this is still so but it isn't far out.
>
> The suspended ceiling should be ignored in any fire resistance
> estimations.
>
>
>>What about 18mm of chipboard alone?

>
>
> No.
>


Double layer of 12.5mm plaster board does meet 30 min requirement. So
does single layer of 12.5mm firecheck plasterboard which is slightly
pink in colour, but it's very heavy especially in 8x4 sheets.

Nick
 
Reply With Quote
 
 
 
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Advantages Of Drywall For Fire Resistance bluntman001 Home Repair 8 07-02-2011 03:14 AM
Re: Durock fire resistance ? George Building Construction 0 02-01-2006 05:13 PM
Re: Durock fire resistance ? James \Cubby\ Culbertson Building Construction 0 01-30-2006 05:36 AM
Re: Durock fire resistance ? tbasc@bellsouth.net Building Construction 0 01-29-2006 12:31 PM
Re: Durock fire resistance ? Al Bundy Building Construction 0 01-29-2006 05:10 AM


All times are GMT. The time now is 07:32 PM.