Boiler Cutting Out

 
 
Neal Harwood
Guest
Posts: n/a

 
      10-25-2004, 09:24 AM
I have a Potterton Profile 50e boiler, and lately the (thermal?)
cut-out has started tripping. This results in the pump going
continuously, but no hot water.
It happily resets manually, and starts up again.
It seems to trip 4/5 times a week, at different times/conditions - no
obvious pattern.

Any ideas?

Obviously I am not going to take the boiler apart (unqualified), but
if the cause is elsewhere in the system, I beleive I could fix it.

Neal
 
Reply With Quote
 
 
 
 
Set Square
Guest
Posts: n/a

 
      10-25-2004, 10:53 AM
In an earlier contribution to this discussion,
Neal Harwood <(E-Mail Removed)> wrote:

> I have a Potterton Profile 50e boiler, and lately the (thermal?)
> cut-out has started tripping. This results in the pump going
> continuously, but no hot water.
> It happily resets manually, and starts up again.
> It seems to trip 4/5 times a week, at different times/conditions - no
> obvious pattern.
>
> Any ideas?
>
> Obviously I am not going to take the boiler apart (unqualified), but
> if the cause is elsewhere in the system, I beleive I could fix it.
>
> Neal


This normally happens when the boiler and pump are turned off by a room
stat - and the residual heat in the boiler's heat exchanger continues to
heat the water to the point where the overheat stat trips.

Boilers which are susceptible to this usually control the pump directly -
and have an over-run stat which continues to run the pump for a while after
the boiler stops firing - in order to dissipate the residual heat.

Clearly, the water must have an available circulation path during this
over-run period - often requiring a by-pass loop, depending on the exact
setup.

The first thing to check is whether your boiler has a pump over-run stat
and, if so, to make sure that it is wired up correctly.

If you still have problems, come back with further details of your system
setup. Does it look like one of the "plans" described in
http://content.honeywell.com/uk/homes/systems.htm ?

--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.


 
Reply With Quote
 
 
 
 
Andrew Gabriel
Guest
Posts: n/a

 
      10-25-2004, 09:55 PM
In article <(E-Mail Removed)>,
raden <(E-Mail Removed)> writes:
> In message <(E-Mail Removed) >, Neal
> Harwood <(E-Mail Removed)> writes
>>I have a Potterton Profile 50e boiler, and lately the (thermal?)
>>cut-out has started tripping. This results in the pump going
>>continuously, but no hot water.
>>It happily resets manually, and starts up again.
>>It seems to trip 4/5 times a week, at different times/conditions - no
>>obvious pattern.
>>
>>Any ideas?
>>

> The impeller of the pump hasn't broken off the shaft has it ?


or as happened to a friend of mine, the blades had all fallen
off the impeller (and were nowhere to be found).

--
Andrew Gabriel
 
Reply With Quote
 
Set Square
Guest
Posts: n/a

 
      10-25-2004, 10:29 PM
In an earlier contribution to this discussion,
raden <(E-Mail Removed)> wrote:

> In message <(E-Mail Removed) >, Neal
> Harwood <(E-Mail Removed)> writes
>> I have a Potterton Profile 50e boiler, and lately the (thermal?)
>> cut-out has started tripping. This results in the pump going
>> continuously, but no hot water.
>> It happily resets manually, and starts up again.
>> It seems to trip 4/5 times a week, at different times/conditions - no
>> obvious pattern.
>>
>> Any ideas?
>>

> The impeller of the pump hasn't broken off the shaft has it ?


I don't think the system would run for between 1/5 and 1/4 of a week if it
had!

I think it's something to do with sets of circumstances which occur now and
again where the pump can't effectively overrun. Maybe it's not wired to do
so, or maybe there isn't a by-pass and it gets caught out when all the TRVs
are shut.
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.


 
Reply With Quote
 
Neal Harwood
Guest
Posts: n/a

 
      10-26-2004, 08:26 AM
raden <(E-Mail Removed)> wrote in message news:<(E-Mail Removed)>...
> In message <(E-Mail Removed)>, Set Square <(E-Mail Removed)>
> writes
> >In an earlier contribution to this discussion,
> >raden <(E-Mail Removed)> wrote:
> >
> >> In message <(E-Mail Removed) >, Neal
> >> Harwood <(E-Mail Removed)> writes
> >>> I have a Potterton Profile 50e boiler, and lately the (thermal?)
> >>> cut-out has started tripping. This results in the pump going
> >>> continuously, but no hot water.
> >>> It happily resets manually, and starts up again.
> >>> It seems to trip 4/5 times a week, at different times/conditions - no
> >>> obvious pattern.
> >>>
> >>> Any ideas?
> >>>
> >> The impeller of the pump hasn't broken off the shaft has it ?

> >
> >I don't think the system would run for between 1/5 and 1/4 of a week if it
> >had!
> >

> You have a point there - I'll try to read threads better in future




Thanks for the replies so far
I believe the pump is fine, because it DOES work most of the time,
just cuts out occasionally.
It has also only started doing this recently. It used to happen VERY
occasionally (2 times per year), but recently it is much more
frequent.

This 'cut-out due to residual heat' sounds very feasible
I will try and work out the circuit type (thanks for the link) and get
back to you

Neal
 
Reply With Quote
 
Neal Harwood
Guest
Posts: n/a

 
      10-26-2004, 08:33 AM
"Set Square" <(E-Mail Removed)> wrote in message news:<(E-Mail Removed)>...
> In an earlier contribution to this discussion,
> Neal Harwood <(E-Mail Removed)> wrote:
>
> > I have a Potterton Profile 50e boiler, and lately the (thermal?)
> > cut-out has started tripping. This results in the pump going
> > continuously, but no hot water.
> > It happily resets manually, and starts up again.
> > It seems to trip 4/5 times a week, at different times/conditions - no
> > obvious pattern.
> >
> > Any ideas?
> >
> > Obviously I am not going to take the boiler apart (unqualified), but
> > if the cause is elsewhere in the system, I beleive I could fix it.
> >
> > Neal

>
> This normally happens when the boiler and pump are turned off by a room
> stat - and the residual heat in the boiler's heat exchanger continues to
> heat the water to the point where the overheat stat trips.
>
> Boilers which are susceptible to this usually control the pump directly -
> and have an over-run stat which continues to run the pump for a while after
> the boiler stops firing - in order to dissipate the residual heat.
>
> Clearly, the water must have an available circulation path during this
> over-run period - often requiring a by-pass loop, depending on the exact
> setup.
>
> The first thing to check is whether your boiler has a pump over-run stat
> and, if so, to make sure that it is wired up correctly.
>
> If you still have problems, come back with further details of your system
> setup. Does it look like one of the "plans" described in
> http://content.honeywell.com/uk/homes/systems.htm ?


Having just read some old (c1998) posts (I Love GOOGLE Groups),
someone else suggested problems with an airlock in the CH system
We HAVE had to drain the system a couple of times over the last year
(to move some pipes and rads in the basement).
Is it possible I have an airlock of some sort? Where would it be?
Would it cause my symptoms? And of course, HOW do I get rid of it?
 
Reply With Quote
 
Set Square
Guest
Posts: n/a

 
      10-26-2004, 09:55 AM
In an earlier contribution to this discussion,
Neal Harwood <(E-Mail Removed)> wrote:

>
> Having just read some old (c1998) posts (I Love GOOGLE Groups),
> someone else suggested problems with an airlock in the CH system
> We HAVE had to drain the system a couple of times over the last year
> (to move some pipes and rads in the basement).
> Is it possible I have an airlock of some sort? Where would it be?
> Would it cause my symptoms? And of course, HOW do I get rid of it?


I doubt if it's that. An air lock after re-filling can prevent any primary
circlation (I've had one!) but once you've got circulation going, any
residual air will usually park itself somewhere where it doesn't do any
major harm - probably in one of the radiators. I don't think an air lock is
likely to cause an intermittent circulation failure.

Of course, I could be wrong . . .
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.


 
Reply With Quote
 
 
 
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Re: Trianco Boiler Cutting Out Constantly John UK DIY 0 12-16-2004 01:11 PM
Re: Trianco Boiler Cutting Out Constantly John UK DIY 0 12-15-2004 12:45 PM
Worcester 24i Combi boiler keeps cutting out Gareth UK DIY 1 10-24-2004 01:54 PM
Boiler cutting out Bob Smith UK DIY 0 12-22-2003 10:47 AM
Boiler cutting out a_mcbride UK DIY 6 12-19-2003 12:34 AM


All times are GMT. The time now is 09:10 PM.